Muckin_Slusher
Digging the same hole for 19 years.
2 wire non-contact prox switch.
We use these quite a bit, and occasionally get this strangeness.
Pepperl&Fuchs brand.
It's supposed to change state when it detects steel. The "contacts" are supposed to be open when no steel is in front of the target, and the "contacts" are supposed to be closed when steel is in front of the target. The green light simply indicates power. The yellow light illuminates when the "contacts" close. I put contacts in quotes, because this doesn't really have dry contacts since it's a 2 wire powered switch somehow.
We shut power off to this piece of equipment, then once power restored, the switch decides to operate backwards.
Watch the video. You will see me plug in the switch and pass a screwdriver in front of the target, then unplug the switch and plug it in again. The second time the switch is operating opposite how it works the first time. The first time I activate the switch, it's working backwards. The second time is how it's supposed to work.
This system works on 120VAC. This condition could not be rectified by changing out the switch (replacements all acted the same way). Situation was rectified by changing out the hardwired socket.
Explain to me why this is happening because I'm at a loss.
This is how it's wired. It's a 2 wire switch. It can somehow operate with a low enough current to not give input to the PLC.
We use these quite a bit, and occasionally get this strangeness.
Pepperl&Fuchs brand.
It's supposed to change state when it detects steel. The "contacts" are supposed to be open when no steel is in front of the target, and the "contacts" are supposed to be closed when steel is in front of the target. The green light simply indicates power. The yellow light illuminates when the "contacts" close. I put contacts in quotes, because this doesn't really have dry contacts since it's a 2 wire powered switch somehow.
We shut power off to this piece of equipment, then once power restored, the switch decides to operate backwards.
Watch the video. You will see me plug in the switch and pass a screwdriver in front of the target, then unplug the switch and plug it in again. The second time the switch is operating opposite how it works the first time. The first time I activate the switch, it's working backwards. The second time is how it's supposed to work.
This system works on 120VAC. This condition could not be rectified by changing out the switch (replacements all acted the same way). Situation was rectified by changing out the hardwired socket.
Explain to me why this is happening because I'm at a loss.
This is how it's wired. It's a 2 wire switch. It can somehow operate with a low enough current to not give input to the PLC.
Im curious how this works only being 2 wire. For the light to come on it needs to have current. Can’t have that if it’s in the open state. Interesting