Which conductors burned to which conductors?Two conductors burnt together. Happened at my buddy's place. Old 3-wire feed to a well shack. The 120v went away and 240v only... Ground/neutral hot and no breakers tripped.
Which conductors burned to which conductors?Two conductors burnt together. Happened at my buddy's place. Old 3-wire feed to a well shack. The 120v went away and 240v only... Ground/neutral hot and no breakers tripped.
What's the scenario that would get you 240V from ground to neutral?
Hot to messenger. Only 3 wires going to the shack.Which conductors burned to which conductors?
I Just did this. Only 60 feet though. Neutral and ground not bonded. Two ground rods. 8' deep 10' apart. Neutral and ground bonded at main panel.So I have a friend looking to put in a sub panel.
So my questions are: Does the sub panel need a ground rod?
Does the sub panel get the neutral and ground tied together.
Does the ground and neutral get tied together at the main panel?
In VA if it matters.
So that’d get you 120v to ground, not 240v, right?
Your neutral burned to one of the hots. Each carry 120v. Or is there a way to actually get 240 from the neutral to ground?
Glad this conversation was brought up, one thing that I "get" now that I struggled with understanding before was "why" ground and neutrals are or aren't bonded.
Please correct me if I'm wrong, but here's my understanding.
Why you bond ground to neutral:
Obvious reason, you want a path for current to go if there's a fault where there's a potential on exposed metal (i.e. the farmer who electrocutes his livestock on accident).
Not so obvious reason, "neutral" isn't held to a specific potential coming off of the transformer on the pole (i.e., it's floating). Bonding it to ground at the first point of disconnect ensures it's potential is held at that of earth ground (which ideally should be zero volts). The reason why you only do this at the first point of disconnect is explained next
Why you don't bond ground to neutral (at a sub panel):
Neutral does not mean zero volts (or zero potential). Neutral is a really bad word that really means return path for current, but that's too many words so we just call it "neutral". Because of this, your "neutral" will have a potential (voltage) on it when current is flowing through it. More current = more voltage. More distance = more voltage. More resistance = more voltage. Right at the bonding point, this voltage will ideally be zero volts, but the further you go from this point the higher the voltage will be based on those things.
Point being, you can't prevent some voltage being present on neutral. And when you have a sub panel that's some distance from the first disconnect, you're going to have "some" voltage on it. What that "some" is depends on the reasons above, but the value matters less than knowing that something will be there.
So here's why the sub panel ground and neutral shouldn't be bonded at the sub panel in any instance. We know there's going to be "some" voltage on the neutral, if we then go ahead and bond ground to neutral at the sub panel, we've created a path for current to go where it's not supposed to go. (Which in this case is through ground and not neutral)
All of your line current should always return through neutral, but bonding ground to neutral at a sub panel ensures that some current will go to ground which at best results in weird things happening as others have mentioned and at worst, can create enough electrical current in the ground, which you walk on, to cause a hazard.
How much of a hazard is certainly a question. One that I'm not going to answer and is sure to be debated, but the whole point being, current code is designed to ensure normal operation has all current returning through neutral while still providing the safety of a path to ground if a fault occurs. I mean, that's the whole purpose of code, right?
So that’d get you 120v to ground, not 240v, right?
Your neutral burned to one of the hots. Each carry 120v. Or is there a way to actually get 240 from the neutral to ground?
Can I really break your brain and tell you that the wires on the poles don't include a neutral
This whole grounding thingy always causes a huge shit-storm of controversy... I opened up a big ass can of worms when I questioned the wisdom of bonding Ham radio ground to the utility. Whew....it is still going on two months later.
But, I will toss in someting that I learned a few months ago when I installed a service entrance and sub pannel on the ranch.
We were 40' to the pad transformer; ran 4-0 4-0 2-0 UHD. Two ground rods connected with #4 copper and bonded at the service entrance neutral.
I got a chance to have a look-see at the transformer while the POCO was landing the UHD. I noticed a ground rod under the transformer that was also bonded to neutral... My take-away from seeing this; the POCO is using the ground and neutral as a return current path. (2-0 neutral/ground conductor).
That I understand.....The primary doesn't have or need a ground....What is really interesting to me is the shared ground and neutral between neighbors.There is no mechanical connection between primary and secondary windings on a transformer. If you have a delta primary its 3 phases and a ground with no neutral. A wye secondary will have 3 phases and xo which is bonded to ground, which establishes neutral, usually bonded to the transformer case, with all the other ground wires and the grounding electrode conductor to the available grounding electrodes.
That I understand.....The primary doesn't have or need a ground....What is really interesting to me is the shared ground and neutral between neighbors.
Got me thinking why we use 2-0 UHD for the neutral, and 4-0 for the hots.
I prefer main breaker style, QO (not homeline), and more spaces.This is the sub panel I was going to use:
HOM816L125PC - Load center, Homeline, 1 phase, 8 spaces, 16 circuits, 125A convertible main lugs, PoN, NEMA1, combo cover | Schneider Electric USA
Schneider Electric USA. HOM816L125PC - Load center, Homeline, 1 phase, 8 spaces, 16 circuits, 125A convertible main lugs, PoN, NEMA1, combo cover.www.se.com
Thoughts?
And it is going inside a currently existing shed, but they are talking about replacing it with a larger pole barn so I dontt want to undersize the feed....
If I am using a ground rod at the sub panel, and I have tied the ground and neutral at the main panel, what do I do with the extended ground in the sub panel since I am not supposed to tie them together (with the ground rod as well) at the sub panel.
Ok,
Slightly confused here.
If I am using a ground rod at the sub panel, and I have tied the ground and neutral at the main panel, what do I do with the extended ground in the sub panel since I am not supposed to tie them together (with the ground rod as well) at the sub panel.
Someone want to draw a diagram that can clear this up for me?
Land the feeder bonding wire and ground rod wire on the bar circled in green. Homeline MLO panel for reference.If I am using a ground rod at the sub panel, and I have tied the ground and neutral at the main panel, what do I do with the extended ground in the sub panel since I am not supposed to tie them together (with the ground rod as well) at the sub panel.
Someone want to draw a diagram that can clear this up for me?
Whelp, based on this description of why to not have the grounds and neutrals tied together on a sub panel I went down to my basement sub panel and had a look at it. Ended up doing a bit of re-work on it last night. Now all of my grounds are on that side-bar bus jobbie with the fault ground coming in from the main, and my neutrals are all on the neutral bars under the breakers where they belong.Glad this conversation was brought up, one thing that I "get" now that I struggled with understanding before was "why" ground and neutrals are or aren't bonded.
Please correct me if I'm wrong, but here's my understanding.
Why you bond ground to neutral:
Obvious reason, you want a path for current to go if there's a fault where there's a potential on exposed metal (i.e. the farmer who electrocutes his livestock on accident).
Not so obvious reason, "neutral" isn't held to a specific potential coming off of the transformer on the pole (i.e., it's floating). Bonding it to ground at the first point of disconnect ensures it's potential is held at that of earth ground (which ideally should be zero volts). The reason why you only do this at the first point of disconnect is explained next
Why you don't bond ground to neutral (at a sub panel):
Neutral does not mean zero volts (or zero potential). Neutral is a really bad word that really means return path for current, but that's too many words so we just call it "neutral". Because of this, your "neutral" will have a potential (voltage) on it when current is flowing through it. More current = more voltage. More distance = more voltage. More resistance = more voltage. Right at the bonding point, this voltage will ideally be zero volts, but the further you go from this point the higher the voltage will be based on those things.
Point being, you can't prevent some voltage being present on neutral. And when you have a sub panel that's some distance from the first disconnect, you're going to have "some" voltage on it. What that "some" is depends on the reasons above, but the value matters less than knowing that something will be there.
So here's why the sub panel ground and neutral shouldn't be bonded at the sub panel in any instance. We know there's going to be "some" voltage on the neutral, if we then go ahead and bond ground to neutral at the sub panel, we've created a path for current to go where it's not supposed to go. (Which in this case is through ground and not neutral)
All of your line current should always return through neutral, but bonding ground to neutral at a sub panel ensures that some current will go to ground which at best results in weird things happening as others have mentioned and at worst, can create enough electrical current in the ground, which you walk on, to cause a hazard.
How much of a hazard is certainly a question. One that I'm not going to answer and is sure to be debated, but the whole point being, current code is designed to ensure normal operation has all current returning through neutral while still providing the safety of a path to ground if a fault occurs. I mean, that's the whole purpose of code, right?
I'm reading the above and trying to wrap my head around it and gotta admit I'm still pretty lost.
Anyone recommend a decent youtube vid that explains it all?
Put your grounds on a separate buss and put all of your new grounds on it as well. Neutrals get their own buss.Ok,
Slightly confused here.
If I am using a ground rod at the sub panel, and I have tied the ground and neutral at the main panel, what do I do with the extended ground in the sub panel since I am not supposed to tie them together (with the ground rod as well) at the sub panel.
Someone want to draw a diagram that can clear this up for me?