aczlan
Good Morning!
Exactly, the ones that work we adjust the overloads to match the individual motors (480V 3 phase fan motors), even between different brands of the same frame size, rpm, and horsepower there will be .3 to .5 amp difference in how much power the motor pulls and we try to adjust to match what the motor is actually pulling when working that so that if the motor goes bad we only have to replace the motor, not the motor and 50-200 feet of wiring.Because there is no way the breaker is actually sized to the running current of the motor. That's not the purpose of a breaker.
The breaker is to protect the wire not the motor.
The "heater" in the starter can be tuned to within the 1 amp tolerance of the motors running current.
We usually have a breaker for the panel, a set of fuses for each group of 2-5 motors, then come out of that to a overload, then a contactor (like a relay, but bigger).
The power to engage the contactor runs through the auxillary contact on the overload so if the overload trips it drops out the contactor.
Then we use the auxiliary contact on the contactor to provide feedback to the PLC that everything is working as expected and there is power going to that particular fan motor.
Aaron Z