Guess I am dumb, should be able to figure this out...
A tenant said his AC quit working, the filter was dirty and they probably ran it too hard so it got condensate in the pan and kicked the wet switch. He unhooked the fucking thing because he was hot thinking it would kick it back on. The switch has dried out and I can not figure out how this was wired.
White is not used
Black was left alone and is at the common for the t-stat and out to the condenser.
Red, green, and orange are unhooked. There is a wiring nut laying there and green looks like it was twisted around either red or orange. At the 24V red spot for the t-stat, on the furnace board, there is a broken off piece of wire where one got ripped out.
The heat works fine, call for ac and the fan and condenser do not run, power is interrupted to the whole unit and I can't figure out why.
Green and orange are the legs of the normally closed switch. Red should be 24v from t-stat. I think I am wired differently than the instructions so that the whole furnace kicks off rather than just the condenser when the switch is tripped. So it should just be disrupting the call from the t-stat.
Any help here?
From the top of that wiring terminal:
R lug - Red is going to T-stat
C lug - White heads to condenser, blue to t-stat, black to wet switch
Y lug - Yello to t-stat, red to condenser
G, W2 and white lugs go to t-stat
A tenant said his AC quit working, the filter was dirty and they probably ran it too hard so it got condensate in the pan and kicked the wet switch. He unhooked the fucking thing because he was hot thinking it would kick it back on. The switch has dried out and I can not figure out how this was wired.
White is not used
Black was left alone and is at the common for the t-stat and out to the condenser.
Red, green, and orange are unhooked. There is a wiring nut laying there and green looks like it was twisted around either red or orange. At the 24V red spot for the t-stat, on the furnace board, there is a broken off piece of wire where one got ripped out.
The heat works fine, call for ac and the fan and condenser do not run, power is interrupted to the whole unit and I can't figure out why.
Green and orange are the legs of the normally closed switch. Red should be 24v from t-stat. I think I am wired differently than the instructions so that the whole furnace kicks off rather than just the condenser when the switch is tripped. So it should just be disrupting the call from the t-stat.
Any help here?
From the top of that wiring terminal:
R lug - Red is going to T-stat
C lug - White heads to condenser, blue to t-stat, black to wet switch
Y lug - Yello to t-stat, red to condenser
G, W2 and white lugs go to t-stat