PAToyota
Red Skull Member
A bit of background first. The natural gas furnace was here when I moved in thirty years ago as of this past July. I added a programmable thermostat to it the first year I was in the house and about a decade ago I swapped the pilot light out for an electronic ignition unit. It gets regular maintenance - basically cleaning and lubrication. This year I did start looking into replacing it - and the air conditioner - next summer for better efficiency. So, of course, after no issues for decades I now have issues...
For the parts replacement below, everything was replaced with units of the same specs - capacitor, relay, transformer. Double checked. Triple checked. Thermostat was a cheap unit just to test control.
So, it started with the fan relay chattering before engaging or not engaging at all. Straightforward enough to replace it. I also replaced the fan capacitor because some reading online said that a failing capacitor can add stress to the relay and they both go out. Replaced both - they're thirty plus years old. Then nothing worked...
Some testing... The burner side of things all works. Thermostat calls for heat, furnace ignites, everything works properly but the fan doesn't come on, so it shuts off again when it starts to overheat. I can jump the power terminal of the relay to the output terminals and the fan comes on. I can jump the terminals from the thermostat and hear the relay click - however, doing so does not send power to the fan...
So I thought I got a bad relay and replaced it again. Same thing. Got out the multi-meter and was concerned that the relay wasn't getting enough power, so replaced the transformer. Just to eliminate possibilities, I also picked up a cheap thermostat in case the fan control got damaged somehow. Nope. Still won't run the fan. I should note that switching the thermostat control for the fan from "auto" to "on" also doesn't do anything - not just that the heat cycle doesn't engage the fan.
If I bypass the fan relay and apply power directly to the fan, everything works as it should except the fan runs constantly instead of turning on and off with the thermostat. So it would seem it is narrowed down to the relay or transformer - right? The two replacement relays were the same make and model from the same supplier, so there is a chance they had a bad run - or that I somehow got the wrong one (not the same make as original, but same exact specifications).
I have to admit at this point that I'm baffled. It's not like it is rocket surgery (wiring diagram attached - arrows to transformer, relay, and capacitor). About the only other options for things being bad are the various limit switches (yellow box), but that should just mean the fan always runs on high and not medium high - right? I do find it odd that wires from the motor are hooked up to the medium low and low terminals on the terminal block, but there is no way to power them. I guess that's just a way of terminating the wires - or possibly set up for another model?
I'm probably missing something obvious, so I'm throwing this out here before making a service call and paying the big bucks to have my error pointed out.
For the parts replacement below, everything was replaced with units of the same specs - capacitor, relay, transformer. Double checked. Triple checked. Thermostat was a cheap unit just to test control.
So, it started with the fan relay chattering before engaging or not engaging at all. Straightforward enough to replace it. I also replaced the fan capacitor because some reading online said that a failing capacitor can add stress to the relay and they both go out. Replaced both - they're thirty plus years old. Then nothing worked...
Some testing... The burner side of things all works. Thermostat calls for heat, furnace ignites, everything works properly but the fan doesn't come on, so it shuts off again when it starts to overheat. I can jump the power terminal of the relay to the output terminals and the fan comes on. I can jump the terminals from the thermostat and hear the relay click - however, doing so does not send power to the fan...
So I thought I got a bad relay and replaced it again. Same thing. Got out the multi-meter and was concerned that the relay wasn't getting enough power, so replaced the transformer. Just to eliminate possibilities, I also picked up a cheap thermostat in case the fan control got damaged somehow. Nope. Still won't run the fan. I should note that switching the thermostat control for the fan from "auto" to "on" also doesn't do anything - not just that the heat cycle doesn't engage the fan.
If I bypass the fan relay and apply power directly to the fan, everything works as it should except the fan runs constantly instead of turning on and off with the thermostat. So it would seem it is narrowed down to the relay or transformer - right? The two replacement relays were the same make and model from the same supplier, so there is a chance they had a bad run - or that I somehow got the wrong one (not the same make as original, but same exact specifications).
I have to admit at this point that I'm baffled. It's not like it is rocket surgery (wiring diagram attached - arrows to transformer, relay, and capacitor). About the only other options for things being bad are the various limit switches (yellow box), but that should just mean the fan always runs on high and not medium high - right? I do find it odd that wires from the motor are hooked up to the medium low and low terminals on the terminal block, but there is no way to power them. I guess that's just a way of terminating the wires - or possibly set up for another model?
I'm probably missing something obvious, so I'm throwing this out here before making a service call and paying the big bucks to have my error pointed out.