I picked up a new to me toy last weekend. A Langmuir XL Pro CNC table with a Hypertherm 45xp plasma cutter, an air chiller and an array of air filters.
I can read the instructions and wire it as it says, but I don't get electrical/electrical electronics enough to understand its requirements.
The plasma cutter has a 10 AWG 3-wire power cord coming out the back of it with a 50 amp plug (NEMA 6-50P). The manual says I need 50 amp breaker in the panel and a 8 (or 6) AWG wire from the box to the outlet because it's right at 50' in length. I dont understand why the 50 amp breaker and 8 or 6 AWG for 50 amp when the plasma cutter's cord is rated for 30A. Does that 6' of 10 AWG not matter because it's short?
2nd electrical question .... I'm at 48' from the panel to the outlet. Thats right at the end of the 8 AWG capability according to the manual. Should I stick with the 8 or upgrade to the 6 AWG?
I can read the instructions and wire it as it says, but I don't get electrical/electrical electronics enough to understand its requirements.
The plasma cutter has a 10 AWG 3-wire power cord coming out the back of it with a 50 amp plug (NEMA 6-50P). The manual says I need 50 amp breaker in the panel and a 8 (or 6) AWG wire from the box to the outlet because it's right at 50' in length. I dont understand why the 50 amp breaker and 8 or 6 AWG for 50 amp when the plasma cutter's cord is rated for 30A. Does that 6' of 10 AWG not matter because it's short?